(@amstedbill)
Active Member
Joined: 3 years ago
Posts: 3
Topic starter   [#648]

I am evaluating a position step response and need to equate samples to time. Is this the 500 usec position sample time mentioned in the specification, or some other time base?



   
SOLO Team
(@milad)
Illustrious Member Admin
Joined: 7 years ago
Posts: 711
 

Hi @amstedbill, 

Yes, the position loop runs at 500us sample rate.

Milad


If you found the answers helpful and you could solve your problems, please kindly verify here to help others in the future.


   
(@amstedbill)
Active Member
Joined: 3 years ago
Posts: 3
Topic starter  

@milad I understand that the position loop in the controller runs at the 500 usec rate.  What I am aksing about is the sample rate on the x axis of the Monitor in the Motion Terminal.  I need to convert the x axis to time.



   
SOLO Team
(@milad)
Illustrious Member Admin
Joined: 7 years ago
Posts: 711
 

@amstedbill :

In performance monitoring the sampling rate is 500Hz and in Generic one is 200Hz.

let me know if you have any other questions.

Milad

 


If you found the answers helpful and you could solve your problems, please kindly verify here to help others in the future.


   
(@amstedbill)
Active Member
Joined: 3 years ago
Posts: 3
Topic starter  

@milad That's exactly what I needed.  Thank you.